Adding heat- wiring question

Posted: Thu Jul 30, 2020 8:25 am
by ChrisNeilan
I am going to add some electric baseboard heat to my soon to be insulated and “sound proofed” basement shop. Thirty solar panels just went up on my roof! My question is, at 240 volts, what is the maximum wattage that 12 gauge can safely handle?
As always, thanks in advance.
Chris

Re: Adding heat- wiring question

Posted: Thu Jul 30, 2020 8:34 am
by ChrisNeilan
Thanks Dusty. I plan on installing two 1500 watt heaters. I’ll run the wire prior to hitting the walls with spray foam insulation. Great vapor barrier .

Re: Adding heat- wiring question

Posted: Thu Jul 30, 2020 9:15 am
by JPG
#12 awg is 'rated' for 20 A. The voltage is irrelevant, but typical romex etc. is 'rated' 600v.

Did Dusty say something??? :confused:

Re: Adding heat- wiring question

Posted: Thu Jul 30, 2020 9:21 am
by dusty
JPG wrote:#12 awg is 'rated' for 20 A. The voltage is irrelevant, but typical romex etc. is 'rated' 600v.

Did Dusty say something??? :confused:
Yes I did but I deleted it. After rereading my reference, I was uncertain about the number I stated.

Re: Adding heat- wiring question

Posted: Thu Jul 30, 2020 9:21 am
by dusty
JPG wrote:#12 awg is 'rated' for 20 A. The voltage is irrelevant, but typical romex etc. is 'rated' 600v.

Did Dusty say something??? :confused:
Yes I did but I deleted it. After rereading my reference, I was uncertain about the number I stated.

https://www.icmag.com/modules/Tutorials ... y/1655.htm

Local Code????

Re: Adding heat- wiring question

Posted: Thu Jul 30, 2020 9:51 am
by JPG
After reading what dusty referenced;

I would recommend staying below 16A for electric heating supply wiring since long term loading is likely. I would also recommend larger wire size if run is very long.

BTW at 240v @ 16A(resistive) = 3840 W.

2 x 1500W will be safely supplied with #12, but #10 is more gooder if run is very far. 10-2(with #10 ground) will suffice. 10-3(w/o ground) will also do if ground wire is painted/marked. Local codes need to be strictly adhered to fer sure with this project!!!!!!!!!

Re: Adding heat- wiring question

Posted: Thu Jul 30, 2020 10:07 am
by JPG
P.S. I would use #10-2 BX for supply wiring, NOT romex. I assume it still exists.

Re: Adding heat- wiring question

Posted: Mon Jul 11, 2022 11:02 pm
by SpencerWhite
After you’ve figured out the usage, you need to select the technology.

Re: Adding heat- wiring question

Posted: Tue Jul 12, 2022 11:06 pm
by ChrisNeilan
Well, time flies! I did run 10 gauge wire, but never installed any heat. With all the insulation I installed, and the fact that my furnace lives nearby, the temperature never got below 65 degrees! My sleeve unit AC has a heat function, but I only turned it on once over the winter just to see if it works!